AVAYA G3Vi pbx如果温度超过27度就故障 故障时有时候有告警,有时候没有告警,告警的时候显示下面内容:
display errors
HARDWARE ERROR REPORT - ACTIVE ALARMS
Port Mtce Alt Err Aux First Last Err Err Rt/ Al Ac Name Name Type Data Occur Occur Cnt Rt Hr St
01A SW-CTL 1281 11 12/28/19:00 12/29/14:48 18 0 12 a y 01A SW-CTL 1025 12/28/19:00 12/29/14:48 6 0 3 a y 01A SW-CTL 2 12/28/19:00 12/29/14:49 8 0 5 a y 01A SW-CTL 1793 6 12/29/14:28 12/29/14:52 13 32 10 a y
display errors Page 1
HARDWARE ERROR REPORT - ACTIVE ALARMS
Port Mtce Alt Err Aux First Last Err Err Rt/ Al Ac Name Name Type Data Occur Occur Cnt Rt Hr St
01A SW-CTL 1793 8 12/29/15:01 12/29/15:08 26 222 26 a y 01A SW-CTL 2 12/29/15:05 12/29/15:07 5 150 5 a y 01A SW-CTL 1281 11 12/29/15:06 12/29/15:07 12 720 12 a y 01A SW-CTL 1025 12/29/15:06 12/29/15:08 4 120 4 a y
test network-control
TEST RESULTS
Port Maintenance Name Alt. Name Test No. Result Error Code
01A DATA-BD 52 FAIL 01A SW-CTL 95 PASS 01A SW-CTL 92 FAIL 1 01A SW-CTL 94 PASS 01A SW-CTL 324 ABORT 1005 01A CARD-MEM 695 PASS 01A CARD-MEM 696 PASS 01A CARD-MEM 697 PASS 01A CARD-MEM 698 PASS 01A CARD-MEM 699 PASS
TEST RESULTS
Port Maintenance Name Alt. Name Test No. Result Error Code
PN 01A TDM-BUS 294 ABORT 1115 PN 01A TDM-BUS 296 FAIL PN 01A TDM-BUS 297 ABORT 1005 PN 01B TDM-BUS 294 ABORT 2000 PN 01B TDM-BUS 296 ABORT 1005 PN 01B TDM-BUS 297 ABORT 1001
ECOMPRESSING IDATA in_cnt = 652052, out_cnt = 2445312
故障现象:
每次故障,机房内的空调显示温度都超过27度,数字话机和话务台没有任何显示,就像断开PN2401板卡一 样,故障的有时候模拟话机可以拨号和被叫,有时候就有拨号音,但是不能拨号。接下来,降底机房的温
度,观察几次,温度到了25度一下,10分钟内,pbx设备自动恢复正常;根据该交换机的使用要求,0-40
度的温度范围,不应该出现这样的问题的,
请教一下,这个问题在哪里呀?谢谢! |