<P>CARE中有一英语词组:discharge air temperature,各位强人,用中文怎么表达啊?</P>
<P>以下是原文:</P>
<P >Calculate optimized values for starting and stopping the heating plant. The EOH functiontakes into account the residual heat in a building to avoid unnecessary heating operation and, thus, save energy. Required room conditions are met at all times.<p></p></P>
<P > <p></p></P>
<P ><FONT face=Helvetica>EOH calculates required flow temperature with an integrated heating curve.<p></p></FONT></P>
<P ><FONT face=Helvetica> <p></p></FONT></P>
<P ><FONT face=Helvetica>Two techniques are available:<p></p></FONT></P>
<P > <p></p></P>
<P >• optimization without room sensor<p></p></P>
<P >• optimization with room sensor.<p></p></P>
<P > <p></p></P>
<P ><FONT face=Helvetica>Optimization without a room sensor uses outdoor air temperature to determine optimum start (the preheat point).<p></p></FONT></P>
<P ><FONT face=Helvetica> <p></p></FONT></P>
<P ><FONT face=Helvetica>Optimization with a room sensor uses room control and needs a time constant and dead time to calculate the preheat point. In other words, this type of optimization requires a Time Program.<p></p></FONT></P>
<P > <p></p></P>
<P ><FONT face=Helvetica>Time program setpoint default values:<p></p></FONT></P>
<P > <p></p></P>
<P >• actual setpoint,<p></p></P>
<P >• next setpoint<p></p></P>
<P >• time until the next setpoint<p></p></P>
<P > <p></p></P>
<P > The EOH function sets these values during processing via the user address.<p></p></P>
<P > <p></p></P>
<P ><FONT face=Helvetica>If optimization in the Time Program is inactive (OPTIM field), the room temperature setpoint is valid for the user address and software calculates the heating <FONT color=#ee1111>discharge air temperature</FONT> using the heating curve.<p></p></FONT></P>
<P > <p></p></P>
|
|