各位楼控达人,下面是一个空调机组的控制案例,哪位能给逐条解释一下,多谢!
00010 C LOW TEMP ALAM
00020 IF ("EY-F2-1QAF") THEN GOTO 130
00030 IF ("EY-F2-1FA" .EQ. OFF) THEN GOTO 190
00040 C FAN RUN
00050 ON ("EY-F2-1DMP1","EY-F2-1DMP2")
00060 IF (SW2 .EQ. OFF) THEN GOTO 100
00070 C SUMMER VALVE CONTROL
00080 LOOP (0,"EY-F2-1HT","EY-F2-1CV","EY-F2-1TSET",3000,200,0,2,0,0,100,0)
00090 GOTO 230
00100 C WINTER VALVE CONTROL
00110 LOOP (128,"EY-F2-1HT","EY-F2-1CV","EY-F2-1TSET",3000,200,0,2,0,0,100,0)
00120 GOTO 230
00130 C LOW DETECT
00140 OFF ("EY-F2-1CMD")
00150 RELEAS (@OPER,"EY-F2-1CMD","EY-F2-1CV","EY-F2-1DMP1")
00160 SET (100,"EY-F2-1CV")
00170 IF ("EY-F2-1FA" .EQ. OFF) THEN OFF ("EY-F2-1DMP1")
00180 GOTO 230
00190 C FAN STOP
00200 OFF ("EY-F2-1DMP1")
00210 IF (SW2) THEN SET (0,"EY-F2-1CV") ELSE SET(0,"EY-F2-1CV")
00220 OFF ("EY-F2-1XDCMD")
00225 ON ("EY-F2-1DMP2")
00230 GOTO 10
|